A breaker that trips is reporting a problem. We test the circuit first. Replacing it without finding out why just removes the warning. A worn breaker that trips below its rating is a replacement. Breaker replacement on an accessible panel starts from $300. No minimum job.
Buzzing panels: a buzz, a crackle, or a hum that got louder usually means a loose connection arcing at a breaker, the bus, or the main lugs. Loose lugs are the most common cause of heat in a panel. We check them and tell you what we found before we fix it.
A bad breaker, a loose lug, or a corroded neutral bar is a repair. A panel that is rusted through, out of space, or a Federal Pacific or Zinsco is an upgrade.
Book online or call to get on the schedule. We answer calls 7 days a week, 5 AM to 11:30 PM, and book you into the next available appointment.
Diagnostic call
$200 – $500
Tracking down why a breaker keeps tripping, a circuit is dead, or lights flicker. Depends on time required.
Connection & bus repair
$250 – $600
Re-terminating loose or heat-damaged conductors, clearing double-taps, neutral and ground bar work.